As a move through the 2018 IEBC for a historic building I am a little puzzled. I have an historic building, undergoing a change of occupancy, with restoration and repair (no alterations". IEBC 401.1 says repairs to a historic building need only comply with ch. 12. Ch. 12 allows repairs and replacement to use like materials and methods. Since this section clearly says that repairs only need comply with ch. 12 then does 305 apply?
305.1 says 305.1 through 305.9 applies to maintenance (undefined), C of O's, additions, and alterations, including historic buildings. By this I take it that repairs are not required to comply with 305, but C of O's are. If the C of O brings 305 in, then 305.4.2 would require 1 accessible entrance, and 1 accessible route. 305.7 tells us that where an alteration affects or contains an area of primary function, then the accessible route must be provided, with the 20% exception. Since there are not alterations occurring, then this section wouldn't seem to apply. Am I then left with 305.4.2 which requires the accessible route and entrance without a 20% exception? That seems counter-intuitive because it seems to say that if your are doing less inside, you must do more outside.
The building has no accessible route or entrance. It is an old two-room dwelling, being minimally restored for use "used for tours (museum)" which is their description in the scope of work. My first reaction was to require an accessible route and entrance, even though no alterations are occurring to the entrance or accessible route. But since only repairs are occurring to the primary function area I am second-guessing this.
I am thinking 305 applies, because the project includes repairs AND a C of O. If this is correct I think 305.4.2 requires the accessible route and entrance, but doubt creeps in because if the were altering the primary function they would only need to comply up to 20%.
I have toured similar facilities, and can't recall for sure but don't think they had accessible entrances or routes, but maybe that was different since they were the homes of presidents, way more historically significant than a small town shack in a city park.
Any guidance or experience is appreciated.
305.1 says 305.1 through 305.9 applies to maintenance (undefined), C of O's, additions, and alterations, including historic buildings. By this I take it that repairs are not required to comply with 305, but C of O's are. If the C of O brings 305 in, then 305.4.2 would require 1 accessible entrance, and 1 accessible route. 305.7 tells us that where an alteration affects or contains an area of primary function, then the accessible route must be provided, with the 20% exception. Since there are not alterations occurring, then this section wouldn't seem to apply. Am I then left with 305.4.2 which requires the accessible route and entrance without a 20% exception? That seems counter-intuitive because it seems to say that if your are doing less inside, you must do more outside.
The building has no accessible route or entrance. It is an old two-room dwelling, being minimally restored for use "used for tours (museum)" which is their description in the scope of work. My first reaction was to require an accessible route and entrance, even though no alterations are occurring to the entrance or accessible route. But since only repairs are occurring to the primary function area I am second-guessing this.
I am thinking 305 applies, because the project includes repairs AND a C of O. If this is correct I think 305.4.2 requires the accessible route and entrance, but doubt creeps in because if the were altering the primary function they would only need to comply up to 20%.
I have toured similar facilities, and can't recall for sure but don't think they had accessible entrances or routes, but maybe that was different since they were the homes of presidents, way more historically significant than a small town shack in a city park.
Any guidance or experience is appreciated.