• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NEC 250.54 Auxiliary Grounding Electrodes Clarified

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,064
Location
Somewhere Too Hot & Humid
The code reads:

250.54 Auxiliary Grounding Electrodes.
One or more grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.53(A)(2) Exception, but the earth shall not be used as an effective ground-fault current path as specified in 250.4(A)(5) and 250.4(B)(4).

The code means:

Grounding electrodes, such as ground rods, that are connected to equipment are not permitted to be used in lieu of the EGC, but grounding electrodes may be used to establish a reference to ground in the area of electrically operated equipment. The earth may not be used as the EGC or effective (ground) fault current path. Auxiliary grounding electrodes are not required to be incorporated into the grounding electrode system for the service or other source of electrical supply.
 