NEC 334 Securing and Supporting NM Cable

jar546

CBO
Joined
Oct 16, 2009
Messages
12,718
Location
Not where I really want to be
334.30 Securing and Supporting.

Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties listed and identified for securement and support, or straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (41⁄2 ft) and within 300 mm (12 in.) of every cable entry into enclosures such as outlet boxes, junction boxes, cabinets, or fittings. The cable length between the cable entry and the closest cable support shall not exceed 450 mm (18 in.). Flat cables shall not be stapled on edge.

Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.

IMG_1302.JPG
 
I think this installation is illustrated is in the "Romex Kings Guide to Wiring" Volume II manual? Not sure what happen to my copy?

I would be okay with the install.
 