First, let's look at some of the primary verbiage of this section below. I think the most important part is where it says "Emergency lighting systems shall be designed and installed so that the failure of any individual lighting element, such as the burning out of a lamp, cannot leave in total darkness any space that requires emergency illumination."
So, if during final inspection, I go to the breaker box and shut down the circuit, emergency lights should come one, correct?
What happens when you find no emergency lights and the contractor tells you that they have an emergency generator. Would that meet the requirements of NEC 700.16?
So, if during final inspection, I go to the breaker box and shut down the circuit, emergency lights should come one, correct?
What happens when you find no emergency lights and the contractor tells you that they have an emergency generator. Would that meet the requirements of NEC 700.16?
700.16 Emergency Illumination.
Emergency illumination shall include means of egress lighting, illuminated exit signs, and all other luminaires specified as necessary to provide required illumination.
Emergency lighting systems shall be designed and installed so that the failure of any individual lighting element, such as the burning out of a lamp, cannot leave in total darkness any space that requires emergency illumination.
Where high-intensity discharge lighting such as high- and low-pressure sodium, mercury vapor, and metal halide is used as the sole source of normal illumination, the emergency lighting system shall be required to operate until normal illumination has been restored.
Where an emergency system is installed, emergency illumination shall be provided in the area of the disconnecting means required by 225.31 and 230.70, as applicable, where the disconnecting means are installed indoors.