• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NEC True or False Question: Receptacles

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,064
Location
Somewhere Too Hot & Humid
True or False:
Receptacles rated at 20 amperes or less and designed for the direct connection of aluminum conductors must be marked CO/ALR, and if they are not CO/ALR type, they can be connected to an aluminum branch-circuit conductor using a copper pigtail with a wire connector
 
True, if the wire connector is rated for copper and aluminum together (which is its own story). The UL guide for receptacles (RTDV) says in part:

"Terminals of 15 and 20 A receptacles not marked ‘‘CO/ALR’’ are for use with copper and copper-clad aluminum conductors only. Terminals marked ‘‘CO/ALR’’ are for use with aluminum, copper and copper-clad aluminum conductors."

But this is more of a UL guide quiz than an NEC quiz.

Cheers, Wayne
 