This is an all too common violation whenever you have a gutter that contains service conductors. You mostly see this whenever you have multiple service disconnects on one building. According to NEC 250.24(A)(1):
(1) General. The grounding electrode conductor connection
shall be made at any accessible point from the load end of the
overhead service conductors, service drop, underground service
conductors, or service lateral to, including the terminal or
bus to which the grounded service conductor is connected at
the service disconnecting means.
Informational Note: See definitions of Service Conductors, Overhead;
Service Conductors, Underground; Service Drop; and Service
Lateral in Article 100.
There are essentially 3 points that the GEC can connect to: 1) The load end of the service drop on a mast which is impractical, 2) At the meter can where the neutral connects to the meter enclosure, or 3) The terminal or bus bar where the neutral lands on the service disconnect.
In this case, they decided to land the GEC on the trough, therefore violating NEC 250.24(A)(1). To remedy this situation, the GEC would have to be connected to the same P-Tap as the service neutral where it enters this enclosure.
(1) General. The grounding electrode conductor connection
shall be made at any accessible point from the load end of the
overhead service conductors, service drop, underground service
conductors, or service lateral to, including the terminal or
bus to which the grounded service conductor is connected at
the service disconnecting means.
Informational Note: See definitions of Service Conductors, Overhead;
Service Conductors, Underground; Service Drop; and Service
Lateral in Article 100.
There are essentially 3 points that the GEC can connect to: 1) The load end of the service drop on a mast which is impractical, 2) At the meter can where the neutral connects to the meter enclosure, or 3) The terminal or bus bar where the neutral lands on the service disconnect.
In this case, they decided to land the GEC on the trough, therefore violating NEC 250.24(A)(1). To remedy this situation, the GEC would have to be connected to the same P-Tap as the service neutral where it enters this enclosure.