Tenant fit out in Existing Building
Tenant has leased a portion of the building where the finished floor is 3 or 4 feet above grade. The interior doors have been locked / removed / made inoperable. Any accessibility the space once had is now gone.
Is an accessible entrance (and route from the parking lot) required in its entirety per 3411.8.1 (code section listed below) or can the tenant utilize the Exception 1 (20% rule) from 3411.7 to only provide part of an accessible entrance and route?
FWIW, it does not matter to me which code section takes precedence; I just want to give the correct answer to our client.
Thanks in advance.
3411.8.1 Entrances. Accessible entrances shall be provided in accordance with Section 1105.
Exception: Where an alteration includes alterations to an entrance, and the building or facility has an accessible entrance, the altered entrance is not required to be accessible, unless required by Section 3411.7. Signs complying with Section 1110 shall be provided.
3411.7 Alterations affecting an area containing a primary function. Where an alteration affects the accessibility to, or contains an area of primary function, the route to the primary function area shall be accessible. The accessible route to the primary function area shall include toilet facilities or drinking fountains serving the area of primary function.
Exceptions:
1. The costs of providing the accessible route are not required to exceed 20 percent of the costs of the alterations affecting the area of primary function. 2. This provision does not apply to alterations limited solely to windows, hardware, operating controls, electrical outlets and signs. 3. This provision does not apply to alterations limited solely to mechanical systems, electrical systems, installation or alteration of fire protection systems and abatement of hazardous materials. 4. This provision does not apply to alterations undertaken for the primary purpose of increasing the accessibility of an existing building, facility or element.
Tenant fit out in Existing Building
Tenant has leased a portion of the building where the finished floor is 3 or 4 feet above grade. The interior doors have been locked / removed / made inoperable. Any accessibility the space once had is now gone.
Is an accessible entrance (and route from the parking lot) required in its entirety per 3411.8.1 (code section listed below) or can the tenant utilize the Exception 1 (20% rule) from 3411.7 to only provide part of an accessible entrance and route?
FWIW, it does not matter to me which code section takes precedence; I just want to give the correct answer to our client.
Thanks in advance.
3411.8.1 Entrances. Accessible entrances shall be provided in accordance with Section 1105.
Exception: Where an alteration includes alterations to an entrance, and the building or facility has an accessible entrance, the altered entrance is not required to be accessible, unless required by Section 3411.7. Signs complying with Section 1110 shall be provided.
3411.7 Alterations affecting an area containing a primary function. Where an alteration affects the accessibility to, or contains an area of primary function, the route to the primary function area shall be accessible. The accessible route to the primary function area shall include toilet facilities or drinking fountains serving the area of primary function.
Exceptions:
1. The costs of providing the accessible route are not required to exceed 20 percent of the costs of the alterations affecting the area of primary function. 2. This provision does not apply to alterations limited solely to windows, hardware, operating controls, electrical outlets and signs. 3. This provision does not apply to alterations limited solely to mechanical systems, electrical systems, installation or alteration of fire protection systems and abatement of hazardous materials. 4. This provision does not apply to alterations undertaken for the primary purpose of increasing the accessibility of an existing building, facility or element.