Architect1281
REGISTERED
Had a wise designer today tell me that due to design provided space in this code section that they would not need to provide R-38 per zone 5 but could use R-30
N1102.2.2 Ceilings without attic spaces.
Where Section N1102.1 would require insulation levels above R-30 and the design of the roof/ceiling assembly does not allow sufficient
space for the required insulation, the minimum required insulation for such roof/ceiling assemblies shall be R-30.
This reduction of insulation from the requirements of Section 402.1.1shall be limited to 500 square feet (46 m2) of ceiling area. This reduction shall not apply to the U-factor
alternative approach in Section N1102.1.2 and the Total UA alternative in Section N1102.1.3
Designer provided a 2x10 sloped ceiling / cathedral design and said the space was inadequate to put in the 123" R-38 fiberglass batt.
I told them that the space designed was sufficient to incorporate the required R-38 insulation and they just chose the WRONG INSULATION material.
Install 2# closed cell poly expanding foam which in that space and it would be near R-50 so put in enough to attain R-38; says I
Agree or disagree? but the space seem to be of sufficient space to comply? No Es Verdad?
COMPLIANCE IS THE ALTERNATIVE............
N1102.2.2 Ceilings without attic spaces.
Where Section N1102.1 would require insulation levels above R-30 and the design of the roof/ceiling assembly does not allow sufficient
space for the required insulation, the minimum required insulation for such roof/ceiling assemblies shall be R-30.
This reduction of insulation from the requirements of Section 402.1.1shall be limited to 500 square feet (46 m2) of ceiling area. This reduction shall not apply to the U-factor
alternative approach in Section N1102.1.2 and the Total UA alternative in Section N1102.1.3
Designer provided a 2x10 sloped ceiling / cathedral design and said the space was inadequate to put in the 123" R-38 fiberglass batt.
I told them that the space designed was sufficient to incorporate the required R-38 insulation and they just chose the WRONG INSULATION material.
Install 2# closed cell poly expanding foam which in that space and it would be near R-50 so put in enough to attain R-38; says I
Agree or disagree? but the space seem to be of sufficient space to comply? No Es Verdad?
COMPLIANCE IS THE ALTERNATIVE............