New Car Showroom Receptacles

jar546

CBO
Joined
Oct 16, 2009
Messages
12,816
Location
Not where I really want to be
Educational:

A new car dealership has an 8 bay garage for service as part of the main building. There is a doorway that opens from the service garage to the showroom/service counter for the mechanics to drop of paperwork. The garage area has overhead gas heaters in place for the winter but no other HVAC system other than a manually operated exhaust fan.

The owner wants you to install floor receptacles for a new display area in the showroom. Can you?
 
Perhaps I am missing something but why would the showroom be affected by the service garage? I don't see an issue with the receptacle in the showroom.
 
511.2 Definitions.

Major Repair Garage. A building or portions of a building

where major repairs, such as engine overhauls, painting,

body and fender work, and repairs that require draining

of the motor vehicle fuel tank are performed on motor

vehicles, including associated floor space used for offices,

parking, or showrooms. [30A:3.3.12.1]
 
Yes, it would be a Class 1, Division 2 unless there was an air handling system compliant with the 500.5(B)(2)(3)

(3)
spacer.gif
That is adjacent to a Class I, Division 1 location, and to which ignitible concentrations of flammable gases, flammable liquid–produced vapors, or combustible liquid–produced vapors above their flash points might occasionally be communicated unless such communication is prevented by adequate positive-pressure ventilation from a source of clean air and effective safeguards against ventilation failure are provided.

So the answer is no, you cannot install a receptacle on the floor.

The question then becomes, at what height can you install the receptacle?
 
I guess if the ventilation in the showroom meets the demands of 511.3©(1) then it should be okay

(1) Floor Areas.(a) Ventilation Provided. The floor area shall be unclassified where there is mechanical ventilation providing a minimum of four air changes per hour or 0.3 m3/min/m2 (1

cfm/ft2) of exchanged air for each square meter (foot) of floor area. Ventilation shall provide for air exchange across the entire floor area, and exhaust air shall be taken at a

point within 0.3 m (12 in.) of the floor.

(b) Ventilation Not Provided. The entire floor area up to a level of 450 mm (18 in.) above the floor shall be classified as Class I, Division 2 if the ventilation does not

comply with 511.3©(1)(a).
 
Dennis said:
I guess if the ventilation in the showroom meets the demands of 511.3©(1) then it should be okay
Probably not going to happen.

That would require an air change every fifteen minutes. Those cars would be flying out the door.
 
jar546 said:
Yes, it would be a Class 1, Division 2 unless there was an air handling system compliant with the 500.5(B)(2)(3)(3)
spacer.gif
That is adjacent to a Class I, Division 1 location, and to which ignitible concentrations of flammable gases, flammable liquid–produced vapors, or combustible liquid–produced vapors above their flash points might occasionally be communicated unless such communication is prevented by adequate positive-pressure ventilation from a source of clean air and effective safeguards against ventilation failure are provided.

So the answer is no, you cannot install a receptacle on the floor.

The question then becomes, at what height can you install the receptacle?
The hazardous location would only extend up to 18" above the finished floor. The receptacle would have to be located above that.

Chris
 
raider1 said:
The hazardous location would only extend up to 18" above the finished floor. The receptacle would have to be located above that.Chris
Absolutely, I agree. I used an example of a floor receptacle to ensure that the question was concerning a hazardous location.
 