New hotel next to parking garage - windows?

Joined
Oct 19, 2009
Messages
529
Location
Lincoln
Applicable codes: 2012 IBC and 2000 NFPA 101 Life Safety Code

Given that there is an existing parking garage (open parking garage - non-sprinkled) and a stair tower that protrudes above the top parking deck. The local city government owns the parking garage and is willing to sell "air rights" directly above the structure that would allow for new windows that would be located 15 feet from the 3 dimensional property line.

The wall between the parking garage and new hotel will be two-hour rated without openings. This two-hour fire wall will extend upward 15 feet above the parking deck. That portion of the stair tower that protrudes above the parking structure will also be fire-rated where in direct contact with the new hotel. But I am thinking that there will be no additional extension of this fire rating above the roof of the existing elevator shaft and stair tower.

The entire façade from ground level up to the hotel parapet will be used to determine the 45% allowable openings.

The question is whether-or-not windows would be permitted in close proximity to the roof of the stair tower. I am thinking if the roof of the stair tower were to be upgraded to a 2 hour fire rating then it seems obvious that windows would be permissible. But I would also reason that the stair tower is similar to a pedestrian walkway that is built of non-combustible materials and is not polluted with combustible storage materials.

Can the windows having question marks (see attachment) exist just above the stair tower?

Thank you,

ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
 

Attachments

Thanks Ron. I think you nailed it!
Have you ever one first place in anything? And if so, what first place medal are you most proud of?

Meanwhile, I have revised my illustration to show a 30 inch high parapet and wire glass windows where they are located within 10 feet of the roof. Although this may not be necessary if the existing roof can be (or is already) one-hour fire rated.
 