Regrading the New Jersey Rehab sub code Egress question
This is an existing apartment building; the first floor is a single-family residence; second floor has three apartments and the third floor has one apartment. Since its five units it falls under the IBC and the NJ rehab subcode.
The building is not sprinklered
when you exit the two units on the second floor you enter a long corridor with two means of egress, one directly outside to stairs and the other down a set of interior stairs we'd like to demolish the front stairs and provide a second means of egress out of each unit ... is this acceptable or are two means required in the hallway
Any insight would be helpful...thanks
Rehab sub code states:
310.3 Residential Group R-2 Residential Group R-2 occupancies containing sleeping units or more than two dwelling units where the occupants are primarily permanent.
§5:23-6.26 Basic Requirements--Groups R-2 and R-4
6. A single exit is permitted from floor(s) that are not more than 16 feet above grade provided that each dwelling unit on such floors has an operable window with a sill height of not more than 44 inches. (In community residences for the developmentally disabled, the maximum occupant load, excluding staff, is 12.)
7. A single exit is permitted in buildings that are not more than two stories in height from floors that are more than 16 feet above grade with not more than four dwelling units per floor and exit access travel distance not exceeding 50 feet and with a minimum fire resistance rating of one hour for the exit enclosure and opening protectives and provided that each dwelling unit on such floors has an operable window with a sill height of not more than 44 inches. (In community residences for the developmentally disabled, the maximum occupant load, excluding staff, is 12.)
§5:23-6.26A Supplemental Requirements--Groups R-2 and R-4
This is an existing apartment building; the first floor is a single-family residence; second floor has three apartments and the third floor has one apartment. Since its five units it falls under the IBC and the NJ rehab subcode.
The building is not sprinklered
when you exit the two units on the second floor you enter a long corridor with two means of egress, one directly outside to stairs and the other down a set of interior stairs we'd like to demolish the front stairs and provide a second means of egress out of each unit ... is this acceptable or are two means required in the hallway
Any insight would be helpful...thanks
Rehab sub code states:
310.3 Residential Group R-2 Residential Group R-2 occupancies containing sleeping units or more than two dwelling units where the occupants are primarily permanent.
§5:23-6.26 Basic Requirements--Groups R-2 and R-4
6. A single exit is permitted from floor(s) that are not more than 16 feet above grade provided that each dwelling unit on such floors has an operable window with a sill height of not more than 44 inches. (In community residences for the developmentally disabled, the maximum occupant load, excluding staff, is 12.)
7. A single exit is permitted in buildings that are not more than two stories in height from floors that are more than 16 feet above grade with not more than four dwelling units per floor and exit access travel distance not exceeding 50 feet and with a minimum fire resistance rating of one hour for the exit enclosure and opening protectives and provided that each dwelling unit on such floors has an operable window with a sill height of not more than 44 inches. (In community residences for the developmentally disabled, the maximum occupant load, excluding staff, is 12.)
§5:23-6.26A Supplemental Requirements--Groups R-2 and R-4
the building is not sprinklered and there are no fire walls.