• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NFPA 13 Janitors Closet

Rick436

Member
Joined
Jan 23, 2010
Messages
2
Greetings All,

I have a locked janitors closet measuring approximately 4'x4' which has a mop sink inside. The closet is currently not sprinklered. It is located within a sprinklered public restroom of a commercial building. We are remodeling the restroom. Does the existing janitors closet need a sprinkler head?

Thanks for your time.

Rick
 
Re: NFPA 13 Janitors Closet

Rick436,

Welcome to the board!

Don’t believe a Janitor Closet in a commercial building meets the omission allowances in Chapter 8 of NFPA 13, 2002 if you’re in the 06 IBC and 4.1 of NFPA 13, 2002 require sprinklers in all areas unless omissions are permitted in other areas of the standard. By the OP information I don’t know if this is a building requiring a sprinkler system from the building code applicable at the time of construction or if the building code applicable at the time of construction permitted ommissions of JC's by some specific section of that code.
 
Re: NFPA 13 Janitors Closet

would say 99 per cent of the time YES

should have been done when it was orignally sprinkled, unless the closet was added during a remodel and the sprinkler system not modified.

It should have also been noted by the fire sprinkler company during the annual inspections done, and brought to the attention of the owner to have a head added
 