• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NFPA 13D fire dept. connection

Inspector 102

Silver Member
Joined
Oct 22, 2009
Messages
356
Location
N/E Indiana
When a dwelling uses NFPA 13D for the installation guidelines, does it require a fire department connection if the water supply requirements consider fire and domestic fire flow. I do not have 2010 standard available. No current local ordinance addressing the installation requirements. Any comments appreciated.
 
NFPA 13D does not require a fire department connection (FDC). However, if an FDC is provided, the system must pass a hydrostatic pressure test per NFPA 13.
 