• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NFPA 72 Listing of Notification Appliances

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,064
Location
Somewhere Too Hot & Humid
The code reads:

18.3.1 Listing.
All notification appliances installed in conformity with Chapter 18 shall be listed for the purpose for which they are used.


What it means is:

The listing of notification appliances must be use-specific. That is, the listing of an appliance must relate to the way it will be used. This requirement correlates with the requirements of 10.3.1 and 10.3.2, which also require fire alarm system components to be installed in accordance with the manufacturers’ published instructions. These instructions are considered by the listing organization. For example, visual notification appliances listed for wall mounting are not permitted to be installed on a ceiling (or horizontally suspended below the ceiling) because they are designed, tested, and listed for a specific vertical orientation to cover a specific area. If such appliances are mounted horizontally, such as on a ceiling, they will produce inadequate coverage. Appliances listed for ceiling mounting would be required for that application. Visual appliances listed for ceiling mounting can be suspended from the ceiling as permitted by 18.5.5.7.6.
 
Top