nfpa 72 question

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,962
Location
Basement
A manual pull station is pulled.

Is there anything in 72 or something else that states the maximum time it takes before the notification devices activate???
 
Yes, somewhere in the 15 second range if I remember correctly... stand by _ I will get back to you. Also what edition are you using?

2013 edition - 10.12 Alarm Signals.

10.12.1

Actuation of alarm notification appliances or emergency voice communications, emergency control functions, and annunciation at the protected premises shall occur within 10 seconds after the activation of an initiating device.
 
Last edited by a moderator:
Saw this but looked more like a performance

Response time between alarm initiation (contact closure) and

recording at the main fire alarm control unit (appearance on

alphanumeric read out) shall not exceed 5 seconds.
 