NM in hot attic of 142 deg F
Can you install NM in this application?
If you can derate from the 90 deg column but cannot have a rating higher than the 60 degree column, how can you derate from the 90 when it is not allowed in the 60 and there is no number there, only a dash?
"If you always do what is right to others you can't go wrong"
The more I learn, the more I realize just how much I don't know.
334.80 Ampacity. The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The ampacity shall be in accordance with the 60°C (140°F)
conductor temperature rating. The 90°C (194°F) rating
shall be permitted to be used for ampacity derating purposes,
provided the final derated ampacity does not exceed
that for a 60°C (140°F) rated conductor.
I think that means you're SOL.