Typo see footnotes ofTABLE 714.2 OPENING PROTECTIVE FIRE-PROTECTION RATINGS
a. For testing requirements, see Section 714.2.3.
b. Two doors, each with a fire-protection rating of 1.5 hours, installed on opposite sides of the same opening in a fire wall, shall be deemed equivalent in fire-protection rating to one 3-hour fire door.
c. Fire-rated bathroom/restroom doors are not required when opening onto fire-rated halls, corridors, exit access provided:
(1) no other rooms open off of the bathroom/restroom, and
(2) no gas or electric appliances other than electric hand dryers are located in the bathroom/restroom, and
(3) the walls, partitions, floor and ceiling of the bathroom/restroom have a fire rating at least equal to the rating of the hall, corridor or exit access, and
(4) the bathroom/restroom is not used for any other purpose than it is designed.
Read the code don't memorize the numbers