InsideOut
REGISTERED
I'm doing the initial code review for an existing building which will be undergoing a Level 2 alteration. It is a mixed construction type: II-B & III-B. It is under the maximum allowable height and area, and will not be changing its use of B and F-1. It's a two story structure and is fully sprinklered. The building inspector tells me that all of the corridors and stair enclosures must be 1-hour rated, but my reading of the code is that none of them require fire resistance rating. I don't want to go be wrong if I'm going to gainsay the building inspector!
My reasoning is per 1019.3.1, since it's only connecting 2 stories, shaft enclosure is not required and per 1020.1, B and F uses don't require fire resistance rating in the corridor.
Any insight would be greatly appreciated. Thanks!
My reasoning is per 1019.3.1, since it's only connecting 2 stories, shaft enclosure is not required and per 1020.1, B and F uses don't require fire resistance rating in the corridor.
Any insight would be greatly appreciated. Thanks!