"Building element" as defined in section 702: "A fundamental component of building construction, listed in Table 601, which may or may not be of fire - resistive-rated construction and is constructed of materials based on the building type of construction"Section 602.2, 2006 IBC requires many elements of Type I and Type II construction to be of noncombustible materials. There are exceptions of course, that allow combustible construction. For those elements that must be noncombustible, do you allow gypsum wallboard to be used? For instance on walls and floor/ceiling assemblies?
Actually, per 602.2, which references Table 601, "building elements" in Type I and II construction must be of noncombustible materials. We're not talking about fire walls or fire barriers here; let's not confuse fire resistive assemblies with noncombustible assemblies.beach said:I don't believe gypsum wallboard is an element that is required to be non-combustible... I would consider it part of a "Fire-resistance rated" assembly or "Fire Barrier" as defined in section 702.
It does matter. Firewalls (705.5) are to continue to 18" beyond the exterior wall. Exception 1 permit the fire wall to terminate at combustible sheathing if the exterior wall has a 1 hour rating for 4 feet on both side of the firewall. The 3 exceptions to 705.5 give relief from the 18" extension. 705.5.1 reiterates 705.5 Exception 1 (and in a way Exception 2) except at firewalls that intersect at 180 degrees or more.peach said:If the whole building is combustible construction, what difference does it make whether the sheating is FRT or anything else?