2018 Building Codes Illustrated:
"1014.9 Intermediate handrails. Where the occupant load served by a stairway becomes
significant, additional handrails may be necessary to assist stair users. The requirement is
based on the required capacity of the stair established by Section 1005.3.1, not the actual width,
and mandates that at no point shall the required capacity or minimum width be more than
30 inches (762 mm) from a handrail. See Figure 1014-9. It is difficult to determine the exact
point at which intermediate handrails are required, as the handrail projection into the required
width can vary from one design to the next. It should be noted that the measurement is to be
taken in regard to the handrail location, which is permitted to extend a maximum of 4½ inches
(114 mm) into the required width. Where the maximum encroachment occurs on each side
of the stairway, an intermediate handrail must be provided where the required width exceeds
69 inches (1,752 mm). A lesser required width would apply where the handrails do not extend
the full 4½ inches (114 mm) into the minimum required stairway width. As an additional safeguard
for wide monumental stairs, the handrails must be located along the anticipated travel
path of the stair users."
I'm working on an existing plaza project and we're redoing the stairs, redesigning a portion of the plaza as well. When I read this chapter, I'm not quite understanding, for example, If I have a 16'-8" exterior stair from the sidewalk level to the plaza level. How many intermediate handrails would I need?
"1014.9 Intermediate handrails. Where the occupant load served by a stairway becomes
significant, additional handrails may be necessary to assist stair users. The requirement is
based on the required capacity of the stair established by Section 1005.3.1, not the actual width,
and mandates that at no point shall the required capacity or minimum width be more than
30 inches (762 mm) from a handrail. See Figure 1014-9. It is difficult to determine the exact
point at which intermediate handrails are required, as the handrail projection into the required
width can vary from one design to the next. It should be noted that the measurement is to be
taken in regard to the handrail location, which is permitted to extend a maximum of 4½ inches
(114 mm) into the required width. Where the maximum encroachment occurs on each side
of the stairway, an intermediate handrail must be provided where the required width exceeds
69 inches (1,752 mm). A lesser required width would apply where the handrails do not extend
the full 4½ inches (114 mm) into the minimum required stairway width. As an additional safeguard
for wide monumental stairs, the handrails must be located along the anticipated travel
path of the stair users."
I'm working on an existing plaza project and we're redoing the stairs, redesigning a portion of the plaza as well. When I read this chapter, I'm not quite understanding, for example, If I have a 16'-8" exterior stair from the sidewalk level to the plaza level. How many intermediate handrails would I need?