Here are our amendments to 2006 IBC/IFC:
42. Section [F] 903.4, Sprinkler system monitoring and alarms, shall be amended to read as follows:
[F] 903.4 Sprinkler system monitoring and alarms. All valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures, and water-flow switches, shall be electrically supervised by the building fire alarm system.
Exceptions: No change
43. Section [F] 903.4.1, Signals, shall be amended to add to read as follows:
[F] Section 903.4.1 Signals. Alarm, supervisory, and trouble signals shall be distinctly different and automatically transmitted by direct connections to the appropriate fire protection district communication/dispatch center.
44. Section [F] 903.4.2 shall be amended to read as follows:
[F] 903.4.2 Alarms. A fire alarm shall monitor all automatic sprinkler systems. Approved audible and visual devices shall be connected to every automatic sprinkler system. Such sprinkler water-flow alarm devices shall be activated by water flow equivalent to the flow of a single sprinkler of the smallest orifice size installed in the system. Actuation of the automatic sprinkler system shall actuate the building fire alarm system flow alarm, sprinkler bells, and water flow indicating appliances over the fire protection district direct connection. Visual alarm devices shall be arranged so the flashing light beam can be seen at the required level of intensity from all common use areas. Visual alarm appliances shall be provided as directed in Section [F] 907.9.1 and in restrooms. Audible alarms shall be arranged so the alarm can be heard in all areas of the building, as directed in Section [F] 907.9.2.
69. Section [F] 907.9.1.1, Public and common areas, shall be amended to read as follows:
[F] 907.9.1.1 Public and common areas. Visible alarm notification appliances shall be provided in public areas and common areas. A clear weatherproof 75-candela exterior strobe shall be installed on the exterior of all multi-tenant buildings over the main entrance to each tenant space, and shall be activated by the fire alarm devices within that tenant space only. A blue weatherproof 75-candela exterior strobe shall be installed on the exterior of the building above each fire department connection and shall be activated by water flow only.