We have not adopted the 2012 IBC yet, and would like some interpretations from those who are familiar with it.
2 dwelling units per floor, 2500 gross SF per dwelling unit. Travel Distance, CPET NOT an issue.
Section 1021.2.3 allows a a single exit within and from the dwelling unit, provided that it complies with 1015, AND either the exit from the dwelling unit discharges to the exterior at the level of exit discharge, OR the exit access outside the dwelling unit provides access to not less than 2 approved independent exits.
That all makes sense to me.
However, Table 1021.2(1) seems to contradict the section I just quoted, saying that in R-2, basement, 1st, 2nd,and 3rd stories with up to 4 dwelling units can have only one exit from the story.
Is Table 1021.2(1) an exception to Section 1021.2.3? If so, it certainly could have been laid out cleaner.
Thanks in advance for any help.
2 dwelling units per floor, 2500 gross SF per dwelling unit. Travel Distance, CPET NOT an issue.
Section 1021.2.3 allows a a single exit within and from the dwelling unit, provided that it complies with 1015, AND either the exit from the dwelling unit discharges to the exterior at the level of exit discharge, OR the exit access outside the dwelling unit provides access to not less than 2 approved independent exits.