• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

number of fixture units

James Davis

Registered User
Joined
Mar 7, 2018
Messages
19
Location
San Diego Ca.
so the plumbing code tells us how manny toilets we need for a Womens and Mans restrooms but where does it tell us how manny toilets you need per occupant for gender nutral?
 
There is no "gender-neutral" restroom provision in the plumbing (IPC) or building (IBC) codes. The closest thing that these codes have to a "gender-neutral" restroom is the family or assisted-use toilet room. These are only required for Group A and M occupancies and when the aggregate number of water closets for those occupancy groups is 6 or more.
 
You did not say where the project is located.
In California, the IBC has been modified such that any single-occupancy restroom (intended for one user at a time) is designated "gender neutral".
But that doesn't affect the number of fixtures; it only affects the labeling on the door of the restroom.
 
nice spelling
this is in California it is in a county park, it is a two story building with an A3 and a single restroom upstair accessible via an elevator occupant load for the building is 229 they have 5 rest rooms all single usage. one of our inspectors ask (what I thought was a good question for this forum)what would be the required number of toilets based on geneder nutral occupancy.
 
There seem to be several issues inherent in your question:
1. How many fixtures are required to serve 229 occupants?
a) if it was previously legally permitted with the existing # of fixtures you described, and you are not changing the use or occupancy, then the inspector's question about # of fixtures is irrelevant. It "is what it is". Skip to #3 below.
b) if it is a new building, or a change in occupancy or # of users, then you first look to the CPC to determine # of fixtures for male and # of fixtures for female.​
2. If the answer is 1(b) and you have decided to meet the requirements via 100% single occupancy restrooms, then total up the number of required fixtures (male + female), and that's how many single-occupancy (gender neutral) restrooms you will need.

3. See also https://www.documents.dgs.ca.gov/dsa/bulletins/BU_17-01-01.pdf

4. FYI, if new construction, see also CBC 11B-213.2 exception #4, which says 50% of the cluster of single user restrooms must be accessible.
 