• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Occupant load calculation for young kids dance instruction studio

RLM-Architect

Bronze Member
Joined
Oct 24, 2009
Messages
65
Location
Florida Panhandle
Situation:

Proposed renovation of existing building to an instructional dance studio (ballet and such)

7 sf too tight for maneuvering

15 sf too tight for maneuvering

Realistic allowance 50 sf per student seems more reasonable due to the characteristics of ballet (kicking, jumping etc)

Any of you buy in to this 50 sf per student?

Note exercise rooms allow 50 sf per occupant.

I know that is due to equipment in the rooms but then when using equipment, not much movement.

I had a karate school work this way before due to the same issues of space needed for instruction.

These classes are also limited to 20 students at a time which is all an instructor can control in a class of youngsters.
 
Dance studios Occupant load of 15 net square feet per person.

Similar uses to this would be aerobics rooms, basketball courts, gymnastics rooms

.

Exercise rooms that contain stationary bicycles, treadmills, stair steppers, free weights, weight machines, sit-up and stretching stations are counted at 50 gross square feet per occupant
 
I'm inclined, and have calculated before, in line with Mark, the kids are one thing, but the parents are another.
 
mark handler said:
Why would you want less students?Most business operators want more not less students?
So you don't exceed 50 occupants and need a second means of egress, with both doors swinging out, both accessible, and both with illuminated exit signs and emergency egress lighting.
 
Fort said:
So you don't exceed 50 occupants and need a second means of egress, with both doors swinging out, both accessible, and both with illuminated exit signs and emergency egress lighting.
So how often do business operators tell customers "you need to wait outside, until someone else leaves"

The business owner needs to acquire a smaller space or add minimum life safety elements

Or the fire / building officials need to bend the code and risk injuries
 
RLM-Architect said:
Situation:proposed renovation of existing building to an instructional dance studio (ballet and such)

7 sf too tight for maneuvering

15 sf too tight for maneuvering

Realistic allowance 50 sf per student seems more reasonable due to the characteristics of ballet (kicking, jumping etc)

Any of you buy in to this 50 sf per student?

Note exercise rooms allow 50 sf per occupant.

I know that is due to equipment in the rooms but then when using equipment, not much movement.

I had a karate school work this way before due to the same issues of space needed for instruction.

These classes are also limited to 20 students at a time which is all an instructor can control in a class of youngsters.
50 per is code compliant for this exercise class. If putting on recitals with spectators, seating etc. 15 or 7 per would be right.
 
Ahhhh the R,M, or D word that people don't like to use when discussing occupant loads for buildingdesigns........ (Recitals - for dance, Demonstrations/ Matches - for Karate)
How true this statement is! :-o

Before the C. of O. is issued (to the AHJ): Yessir, we promise not to overload the space!

After the C. of O. is issued (to the facility staff): How many more can we jam in here?

.
 
When I was a Code official, I had a bit of a cynical streak in me too.

WHAT IF THEY . . . . ?

1. After more diligent questions on this dance school, the owner has a contract with a local theater (holds up to 1500) for her recitals.

2. After calculating occupant loads in all studios at 15 sf per, the load in the building is still less than 300.

3. CDA - I have never seen a "definition" of exercise room. But NFPA 101 in Table 7.3.1.2 sets Exercise rooms WITH equipment at 50 and WITHOUT equipment at 15 sf per occupant.

4. But also notice that swimming pools are calculated at 50 sf per occupant based on the water surface.

Questions: Is the pool load at 50 based on the need for more space per occupant due to the need for room to perform the various exercise that is typical for swimming?

5. If so, then would it not be logical to allow more than a 3' x 5' area for ballet doe to the space needed for such activity?

Nice discussion. Food for thought.

The trickiest thing Jesus aver bestowed on us was the commandment to love our neighbor as ourselves.

So how do you love yourself? Hope it is a lot, otherwise, your neighbor is in trouble!
 
Any of you buy in to this 50 sf per student?
Yes under 1004.1.1 Exception i have approved dance and martial arts studios at different OL.

I like to use 35 sq ft per person because on average a person with both arms extended and turning 360 degrees will occupy a 6 ft X 6 ft space. This is an acceptable numbers for the day to day operations, Plumbing fixtures HVAC load etc. However I will use 15 for exiting purposes
 
Questions: Is the pool load at 50 based on the need for more space per occupant due to the needfor room to perform the various exercise that is typical for swimming? 5. If so, then would it not be logical

to allow more than a 3' x 5' area for ballet doe to the space needed for such activity?
IMO, the 50 sq. ft. per person occ. load in pools is, because of an increased perception of

fear in a medium that encloses the human body, whereas, a ballet area does not have the

same (perceived) level of fear associated with it, and with the (again, IMO) proximity of

people in water next to other people in the same water, ..that more area is needed, so

that the overcrowding of the water is lessened.

In the few ballet applications that I have seen, there was a row of students warming up

along a wall with their limbs/bodies stretching over the wall mounted, fixed bar. They

did not appear to have the 50 sq. ft. per person as is being lobbied. The warming up

IMO, is different than kicking/jumping/performing.

As somewhat of a code official, I DO have to think "worse case scenario" ( i.e - Section

102.1, 2006 IBC, "..most restrictive shall govern"). History is repleat with thousands of

events where overcrowding of space(s) has led to billions and billions of dollars in losses

(i.e. - property & life). Events that, some, could have been eliminated by proper occupant

loads, egress exits, signage, MOE lighting and on and on and on.

I am not slamming or disrespecting the RDP community, but in most cases, the RDP's

are not there to retrieve the dead or injured bodies of the aftermath.

Since you asked for input on your application, I respectfully offer the 15 sq. ft. per

person occ. loading and all of the requirements that go with it.

Regarding the statement of "loving thy neighbor as ourselves", I will respect the wishes

of this Forum's owner & benevolent benefactor and NOT comment on the spiritual or

political topics. If you want to PM me, please do! :)

Also, ..please keep on posting on here. I, for one, enjoy & respect your input!

This topic is a good one for discussion! Let the banter continue!

.
 
So what about a gymnastics only room with one big mat??

15??? Hard to dance and tumble with only 15 sq ft
 
So what about a gymnastics only room with one big mat?? 15??? Hard to dance and tumble with only 15 sq ft
How many warm up; in the "one big gymanstics room", before dancing and tumbling, or should

we say, "how many CAN warm up in the one big gymnastics room? :devil

.
 
RLM I design them and approve them like this.

1 - USE GROUP B 304.1 - Training and skill development not within a school or academic program < been there for years

2A, TABLE 1004.1.1 Exercise rooms 50 gross 50 is very reasonable (Davinci figure arms out, feet spread, and 1 step any direction consumes 50 sf ant most any size human)

2B Office are 1/100sf

2C Parent waiting or watching Unconcentrated (tables and chairs) net1/15
 