Wakefield47
REGISTERED
I have a group of work stations that need to be enclosed into a private area. The workstation area is 1080 SF and the two offices within the closed space are each 150 SF - making the entire enclosed space 1380 SF. I believe the workstations make this space fixed seating and according to 1004.4 the occupant load is then determined by the number of fixed seats making the occupant load of this space 16 (12 workstations and 2 seats in each office). According to 303.1.1 that means this space is still business occupancy and not pushed to assembly. Is this interpretation correct?
In determining how many doors this space requires: 1029.8 Common Path of Egress Travel states that as an exception if an area serves less than 50 occupants the common path of egress shall not exceed 75'. If this space really only has an occupancy of 16 then I do meet this exception and only need one door. Also since the occupant load I calculated is less than 50 I believe the door can swing in. Can anyone confirm my interpretation of the code is correct?
Thank you!
In determining how many doors this space requires: 1029.8 Common Path of Egress Travel states that as an exception if an area serves less than 50 occupants the common path of egress shall not exceed 75'. If this space really only has an occupancy of 16 then I do meet this exception and only need one door. Also since the occupant load I calculated is less than 50 I believe the door can swing in. Can anyone confirm my interpretation of the code is correct?
Thank you!