Occupant load vs means of egress question

rth

Bronze Member
Joined
Nov 26, 2012
Messages
39
Location
Central MS
ICC IFC 2006 = adopted code

Existing building, old library, 9,710 square footage gross, max occupancy based on 1004.1.1 tabe = 194 (worst case scenario). Egress capacity is 650,

changed to dance hall, same gross square footage, based on 1004.1.1 now occupancy exceeds egress capacity, A-3 > 300 capacity must be sprinkled. Some are saying post occupancy of 300 unsprinkled, others say sprinkle building and post occupancy of 650, others are saying sprinkle the building and make egress capacity meet or exceed occupancy per 1004.1.1.

What is correct?

Thanks,

Richard
 
Current use of space drives the requirements. If the OL requires the installation of a sprinkler system, additionalexits, then it is what is is.
 
Change of use from library to dance hall will bring in a raft of requirements. Is this a dance hall with music and drink aka nightclub? Toilet facilities, exits and sprinklers are all considerations as well as potentially height and area, and accessibility issues.
 
"If Not, post the lower number."

And this will accomplish what? So the BO can say "it was posted" after a incident?

Thanks, but no thanks.
 
Last edited by a moderator:
No penciling the load down.....worst case governs....set by square feet and use of space, then you deal with sprinklers and MOE.....not the other way around....
 
I agree with steveray. The code does not allow you to reduce the occupant load lower than the calculated number.
 
Exception: Where approved by the building official, the actual number of occupants for whom each occupied space, floor or building is designed, although less than those determined by calculation, shall be permitted to be used in the determination of the design occupant load.
 
= $



"Exception: Where approved by the building official, the actual number of occupants for whom eachoccupied space, floor or building is designed, although less than those determined by calculation, shall be

permitted to be used in the determination of the design occupant load."
This may be another case where the BO is directed to let it go!I believe that it is election time in Central Mississippi..........Not the

best time to be ruffling feathers [ i.e. - revenue streams ] with

trivialities such as adopted building & fire codes.

$ =
 
cda said:
Exception: Where approved by the building official, the actual number of occupants for whom each occupied space, floor or building is designed, although less than those determined by calculation, shall be permitted to be used in the determination of the design occupant load.
Where in 06 IFC did you find this?
 
Ibc 2009..

That's it 1004.1.1

Same section on 06 ibc
 
Last edited by a moderator:
cda said:
Exception: Where approved by the building official, the actual number of occupants for whom each occupied space, floor or building is designed, although less than those determined by calculation, shall be permitted to be used in the determination of the design occupant load.
We have the same exception here in Canada, but we also require the occupant load to be posted when this exception is used.
 
I would recommend making use of the maximum requirements and installation of sprinkler systems, additionalexists, etc. This could work out and that should be sufficient.
 
Little late but agree with those who indicate the "change in use" dictates the egress capacity, arrangement of exits and fire protection requirements in accordance with the adopted code that pertains to changes in use :-)
 