On ground pool disconnecting/emergency shut off switch

Mr. Inspector

SAWHORSE
Joined
Nov 28, 2009
Messages
4,657
Location
Poconos/eastern PA
If the pump to an on ground pool is hard wired to comply with the 2015 IRC and the ISPSC if you want the emergency switch and the disconnecting means to be the same switch does the switch need to exactly 5' from the pool?

IRC E4203.3 Disconnecting means. One or more means to
simultaneously disconnect all ungrounded conductors for all
utilization equipment, other than lighting, shall be provided.
Each of such means shall be readily accessible and within
sight from the equipment it serves and shall be located at least
5 feet
(1524 mm) horizontally from the inside walls of a pool,

spa, or hot tub unless separated from the open water by a permanently
installed barrier that provides a 5-foot (1524 mm)
or greater reach path. This horizontal distance shall be measured
from the water’s edge along the shortest path required
to reach the disconnect. (680.12)

ISPSC 313.7 Emergency shutoff switch. An emergency shutoff
switch shall be provided to disconnect power to recirculation
and jet system pumps and air blowers. Emergency shutoff
switches shall be: provided with access; located within sight
of the pool or spa; and located not less than 5 feet (1524 mm)
horizontally from the inside walls of the pool
or spa.
Exception: Onground storable pools, permanent inground
residential swimming pools, residential spas and residential
water features.

Is this an error in the ISPSC and should say at least 5' from the pool?
 
There doesn't seem to be any details about the required emergency switch. Does anyone know anything about if it is to be labeled?

I just did an electrical inspection of a on-ground pool and they had a pump timer on the same pole as the receptacles 6' from the pool. If you open the panel of the timer there is a switch that disconnects power to circulation pump.

Can the switch inside the timer panel be considered the required emergency switch?
 