One hour wall termination

Robert

REGISTERED
Joined
Jan 29, 2016
Messages
348
Location
Pinole, CA
Hello. I need a 1 hour wall because I am less than 5' from property line (CA requires protection on both sides of the wall). The Roof/Clg. assembly is exposed beams with a wood plank ceiling and concealed rafters/insulation above (spray foam insulation...no airspace).At the interior condition: Can the 5/8" type "x" gyp. bd. terminate at the wood plank ceiling (rather than all the way up to the roof sheathing) if we add a second fireblock between the rafters above? I believe that a certain thickness of wood can provide the equivalent fire protection that the gyp. bd. can but am not sure how thick, and if it would even be considered 1 hour. Please see the crude sketch. Thank you.

View attachment 2185

rake.PDF

rake.PDF
 
& : : &

Recommend that you discuss this proposed installation

with the AHJ FCO and or BO, ...to get their input first.

& : : &
 
The inspector suggested adding the additional wood fireblock, though I don't know what thickness will satisfy 1 hour.
 
Thanks will do.

Does the size requirement in Type 4 Heavy Timber construction have anything to do with fire resistance?I believe it does and was going to use that as a guide if I couldn't find any listed assemblies for this condition.
 
Thanks....looks like the NDS has the char rate and depth of sawn lumber that I can apply for a 1 hour rating.
 