This question is related to interior sliding doors, like a closet or office door. Some sliding door hardware is now incorporating a "soft close" mechanism, which catches the door a few inches from closed and closes it softly. Here's a video...the beginning is about installation but at about 55 seconds you can see how it works: Richelieu Hardware - Hardware set for sliding door with soft close - YouTube
The ADA requires sliding doors to open with 5 pounds of force. But there is an advisory that says that this does not apply to the initial force needed to overcome the inertia of the door. Here's the section from the latest ADA guidelines:
404.2.9 Door and Gate Opening Force. Fire doors shall have a minimum opening force allowable
by the appropriate administrative authority. The force for pushing or pulling open a door or gate
other than fire doors shall be as follows:
1. Interior hinged doors and gates: 5 pounds (22.2 N) maximum.
2. Sliding or folding doors: 5 pounds (22.2 N) maximum.
These forces do not apply to the force required to retract latch bolts or disengage other devices that
hold the door or gate in a closed position.
Advisory 404.2.9 Door and Gate Opening Force. The maximum force pertains to the
continuous application of force necessary to fully open a door, not the initial force needed to
overcome the inertia of the door. It does not apply to the force required to retract bolts or to
disengage other devices used to keep the door in a closed position.
The question is, could sliding doors be measured similar to swinging doors...open the door a few inches and then measure the force that's required? Would that meet the intent, in your opinion?
The ADA requires sliding doors to open with 5 pounds of force. But there is an advisory that says that this does not apply to the initial force needed to overcome the inertia of the door. Here's the section from the latest ADA guidelines:
404.2.9 Door and Gate Opening Force. Fire doors shall have a minimum opening force allowable
by the appropriate administrative authority. The force for pushing or pulling open a door or gate
other than fire doors shall be as follows:
1. Interior hinged doors and gates: 5 pounds (22.2 N) maximum.
2. Sliding or folding doors: 5 pounds (22.2 N) maximum.
These forces do not apply to the force required to retract latch bolts or disengage other devices that
hold the door or gate in a closed position.
Advisory 404.2.9 Door and Gate Opening Force. The maximum force pertains to the
continuous application of force necessary to fully open a door, not the initial force needed to
overcome the inertia of the door. It does not apply to the force required to retract bolts or to
disengage other devices used to keep the door in a closed position.
The question is, could sliding doors be measured similar to swinging doors...open the door a few inches and then measure the force that's required? Would that meet the intent, in your opinion?