• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Opening or Penetration?

ajweaver

Bronze Member
Joined
Oct 27, 2009
Messages
41
Location
Austin, TX
Soffit Ventilation-Opening or Penetration

Combustion Air Housings-Opening or Penetration

I am posing these questions in relation to Table R302.1

One jurisdiction in this area is calling the soffit ventilation an opening and having the ventilation

moved to rear and front of house if possible or closed to comply.

Unfortunetly this sucks for ridge vent cross ventilation.

I am unable to find a definition for "opening" or "penetration"

Input?
 
Soffit Ventilation-Opening or Penetration Neither a soffit is a projection from the wall and less than 4 ft requires it to be fire rated. Projections beyond the exterior wall shall not extend more than 12 inches (305 mm) into the areas where openings are prohibited. .

Openings and penetrations from Table R302.1 are refering to the wall not openings or penetrations in a soffit

Combustion Air Housings-Opening or Penetration. An opening if combustible or aluminum materials. A penetration if 26 gauge metal or better
 