2012 IBC is applicable.
Has anyone ever submitted for approval (alternate method) or approved the use of openings per Section 406.5.2 for open parking garages in lieu of the mechanical ventilation per Section 406.6.2 for enclosed parking garages?
I have an apartment building with a small single-story parking garage that is below and adjacent to the dwelling units. The building is Type VB nonseparated occupancies, but the parking garage is unprotected steel. Section 510.7 could possibly be used with the dwelling units classified as Type VB and the parking garage considered an open parking garage and classified as Type IIB. However, Section 510.7.1 appears to require fire barriers and horizontal assemblies for occupancy separations per Table 508.4, which would require the supporting construction of the horizontal assembly to have an equal rating. Since the designer does not want the steel protected, the IBC only requires dwelling unit separation per Section 420, which does not require supporting construction to have an equal rating (Section 711.4, Exception, Item #2).
Thus, leading to my question. If the special provision of Section 510.7 cannot be used and the parking garage is of Type VB construction per the rest of the structure, then it cannot be considered an open parking garage (required to be of Type I, II, or IV construction per Section 406.5.1) and must be considered an enclosed parking garage. Enclosed parking garages are required to have mechanical ventilation per Section 406.6.2. But if open parking garages, with their required minimum openings are not required to have mechanical ventilation, why couldn't enclosed parking garages use the opening requirements of Section 405.5.2 in lieu of the mechanical ventilation?