Certainly appears to be within 3' of the window.Builder Bob said:Only issue may be the clearances from the window
That was my first thought.chris kennedy said:Certainly appears to be within 3' of the window.
I believe the 3' is from an operating portion of a window. Do we know if the top sash operates?chris kennedy said:Certainly appears to be within 3' of the window.
The way I read it if any part of the window opens the entire window would be included in the 3' rule.Yankee said:I believe the 3' is from an operating portion of a window. Do we know if the top sash operates?
230.9 Clearances on Buildings.Service conductors and final spans shall comply with 230.9(A), (B), and ©.
(A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.
Exception: Conductors run above the top level of a window shall be permitted to be less than the 900-mm (3-ft) requirement.