Electrician stripped the SE cable sheathing between the meter cab to the disconnect opposite side of the wall; what code section would you write?
Thanks
Francis
Thanks
Francis
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
310.120 Marking.(A) Required Information. All conductors and cables
shall be marked to indicate the following information, using
the applicable method described in 310.120(B):
(1) The maximum rated voltage.
(2) The proper type letter or letters for the type of wire or
cable as specified elsewhere in this Code.
(3) The manufacturer’s name, trademark, or other distinctive
marking by which the organization responsible for
the product can be readily identified.
(4) The AWG size or circular mil area.
Informational Note: See Conductor Properties, Table 8 of
Chapter 9, for conductor area expressed in SI units for
conductor sizes specified in AWG or circular mil area.
(5) Cable assemblies where the neutral conductor is small
Thanks that's what I needed. I was editing my response when you replied!Dennis said:Francis, is the se cable in conduit? If so I would say that the conductors must be marked and generally they are not marked inside a cable