314.19 Boxes Enclosing Flush Devices. Boxes used to
enclose flush devices shall be of such design that the
devices will be completely enclosed on back and sides
and [b]substantial support for the devices will be provided[/b].
Screws for supporting the box shall not be used in
attachment of the device contained therein.
314.20 In Wall or Ceiling. In walls or ceilings with a
surface of concrete, tile, [b]gypsum[/b], plaster, or other
noncombustible material, boxes employing a flush-type
cover or faceplate shall be installed so that the front edge
of the box, plaster ring, extension ring, or listed extender
will not be set back of the finished surface more than 6
mm (¼ in.).
[b]In walls and ceilings constructed of wood or other
combustible surface material[/b], boxes, plaster rings,
extension rings, or listed extenders shall be flush with the
finished surface or project therefrom.
406.5 Receptacle Mounting. Receptacles shall be
mounted in boxes or assemblies designed for the purpose,
and such boxes or assemblies shall be securely fastened in
place unless otherwise permitted elsewhere in this Code.
(A) Boxes That Are Set Back. Receptacles mounted in
boxes that are set back from the finished surface as
permitted in 314.20 [B]shall be installed such that the
mounting yoke or strap of the receptacle is held rigidly at
the finished surface.[/B]
(B) Boxes That Are Flush. Receptacles mounted in
boxes that are flush with the finished surface or project
therefrom shall be installed such that the mounting yoke
or strap of the receptacle is held rigidly against the box or
box cover.