Rick18071,
From the 2008 NEC, Article 300.9:
"Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of these
raceways shall be considered to be a wet location. Insulated conductors and cables
installed in raceways in wet locations abovegrade shall comply with 310.8©."
Article 310.8©:"Wet locations. Insulated conductors and cables used in wet
locations shall comply with one of the following: (1) Be moisture-impervious
metal-sheathed, (2) Be types MTW, RHW, RHW-2, TW, THW, THW-2, THHW,
THWN, THWN-2, XHHW, XHHW-2, ZW, (3) Be of a type listed for use in wet
locations
Table E3701.4, in the 2006 IRC - ALLOWABLE APPLICATIONS FOR WIRING
METHODS: See the column for NM conductors, ..not allowed in damp [ or wet ]
applications.
Does this help?
.