Given a subpanel fed with 6-3 NM, what is the proper overcurrent device size?
Code says ampacity of NM to be based on 60C.
60C says 55A for #6.
Inspector says must be protected at 50A.
Contractor asks me to look.
Seems to me it is allowed to be protected at 60A per E3605.5.2?
Thanks,