IBC 2024
IEBC 2024
Group B occupancy
Multistory office building with elevator
Building remodel project -- Level 3
Building has a partially exposed floor level that currently has only one existing egress path / door, plus the existing elevator.
We've proposed adding a new door in place of an existing window -- client doesn't like this idea due to some exterior grade issues, however this is actually feasible with a bit of extra work.
There is also a an existing commercial overhead door -- client wants to count this as an egress, and has suggested automatic opening upon fire alarm notification.
To my knowledge, this would not comply, and I'm not reading 1010.3.2 or 1010.3.3 as making this idea acceptable. Any thoughts?
Also, I'm aware of the commercial doors with an integrated person door -- never used them and am not sure of compliance as an egress component?
Thanks in advance.
IEBC 2024
Group B occupancy
Multistory office building with elevator
Building remodel project -- Level 3
Building has a partially exposed floor level that currently has only one existing egress path / door, plus the existing elevator.
We've proposed adding a new door in place of an existing window -- client doesn't like this idea due to some exterior grade issues, however this is actually feasible with a bit of extra work.
There is also a an existing commercial overhead door -- client wants to count this as an egress, and has suggested automatic opening upon fire alarm notification.
To my knowledge, this would not comply, and I'm not reading 1010.3.2 or 1010.3.3 as making this idea acceptable. Any thoughts?
Also, I'm aware of the commercial doors with an integrated person door -- never used them and am not sure of compliance as an egress component?
Thanks in advance.