• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Panic Hardware on Electrical Room

Rider Rick

Silver Member
Joined
Oct 19, 2009
Messages
468
New California School gym electrical room with in-swing door does this meet code?
 
Hi Rick - The article that Charles posted a link to describes the requirements of the National Electrical Code. I'm not sure if CA has adopted different requirements, but per the NEC the door swing and requirements for panic hardware depend on the voltage and amperage of the equipment in the room.
 
1006.2.2.4 Electrical rooms. Electrical rooms shall be provided with exit or exit access doorways in accordance with Section 110.26 of NFPA 70 for electrical equipment rated 1000V or less, and Section 110.33 of NFPA 70 for electrical equipment rated over 1000V.
 