Does part 507.5 apply only to buildings of single occupancy or can it be a mixed use building containing any mix of these occupancies (B, F, M, or S) ?
 
Does part 507.5 apply only to buildings of single occupancy or can it be a mixed use building containing any mix of these occupancies (B, F, M, or S) ?


Year and state for code reference


This section ????

507.5 Two-Story Buildings

The area of a Group B, F, M or S building no more than two stories above grade plane shall not be limited where the building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 and is surrounded and adjoined by public ways or yards not less than 60 feet (18 288 mm) in width.
 
Unlimited area per 507.5 is permitted with mixed use only so long as the listed uses (B, F, M, and S) are the only ones present. The challenge with these large buildings is that you cant throw in an assembly area such as a >750sf conference room, large lunch room, etc.
 
Unlimited area per 507.5 is permitted with mixed use only so long as the listed uses (B, F, M, and S) are the only ones present. The challenge with these large buildings is that you cant throw in an assembly area such as a >750sf conference room, large lunch room, etc.
Thank you for your reply
Is Section 507 to be used in conjunction with occupancies listed in table 506.2 as "UL" or is section 507 separate and apart from the table 506.2?
 