Does part 507.5 apply only to buildings of single occupancy or can it be a mixed use building containing any mix of these occupancies (B, F, M, or S) ?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Does part 507.5 apply only to buildings of single occupancy or can it be a mixed use building containing any mix of these occupancies (B, F, M, or S) ?
Yes, thank youYear and state for code reference
This section ????
507.5 Two-Story Buildings
The area of a Group B, F, M or S building no more than two stories above grade plane shall not be limited where the building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 and is surrounded and adjoined by public ways or yards not less than 60 feet (18 288 mm) in width.
Thank you for your replyUnlimited area per 507.5 is permitted with mixed use only so long as the listed uses (B, F, M, and S) are the only ones present. The challenge with these large buildings is that you cant throw in an assembly area such as a >750sf conference room, large lunch room, etc.
No, it is an alternate to Table 506.2.Thank you for your reply
Is Section 507 to be used in conjunction with occupancies listed in table 506.2 as "UL" or is section 507 separate and apart from the table 506.2?
Thank you !No, it is an alternate to Table 506.2.