A homeowner calls and states they are going to get rid of the concrete around their inground pool deck and replace it with travertine.
Do they need a permit?
Do they need a permit?
A homeowner calls and states they are going to get rid of the concrete around their inground pool deck and replace it with travertine.
Do they need a permit?
What about the fact that the pool perimeter bond is going to be ripped up when they cut out the concrete?It wouldn't here....
Pool perimiter bond electrical inspection.Does muni regulations require a concrete patio to be inspected prior to pouring or a rebar inspection?
Assuming it is there....What code was it built/ installed to?What about the fact that the pool perimeter bond is going to be ripped up when they cut out the concrete?
1987 NEC, or 1981 NECAssuming it is there....What code was it built/ installed to?
Or the 1971 NEC.Assuming it is there....What code was it built/ installed to?
So you are saying the perimeter surfaces have been in there awhile? And the inspector that looked at my pool when I was a kid didn't know anything?Or the 1971 NEC.
Yes. We put a priority on pool electrical safety and pavers around a pool trigger a perimeter bond inspection. Many times we found they were just cut and never connected to anything.So you are saying the perimeter surfaces have been in there awhile? And the inspector that looked at my pool when I was a kid didn't know anything?
Why would this matter. The perimeter surface will be new, so it goes by whatever code you are using now.Assuming it is there....What code was it built/ installed to?
Would you expect them to break into the gunite shell at four locations?Why would this matter. The perimeter surface will be new, so it goes by whatever code you are using now.
Many times someone obtained obtained a permit to replace the deck around a pool? I don't recall having ever experienced that.Many times
If they removed the existing bonding wire, then yes, absolutely. Most of the time they cut the coping and there is always rebar sticking out into the pool deck.Would you expect them to break into the gunite shell at four locations?
Another regional practice that I have never seen. The pool shell is always separated from the deck that surrounds the pool.always rebar sticking out into the pool deck
Technically I don't think bonding the dirt or non-metal perimeter surfaces came in until about 2005.....and as it is required to be 4-6" deep, it wouldn't be in the pavers anyway...Why would this matter. The perimeter surface will be new, so it goes by whatever code you are using now.
I have never inspected a residential pool for a new deck but have for commercial pools. Most of the pools I see are liner pools which would be easy to correct. I have not seen a new gunite shell pool that did not have the rebar continue into the deck. But if they were replacing the deck and there was no accessible spot to connect to the pool rebar, I might make them at least make them connect to the pool rebar at least one place, especially if it was a public pool. I would definitely make sure all the metal ladders, pool pump, pool water and anything else metal within 5' of the water is bonded on any pool.Would you expect them to break into the gunite shell at four locations?