I am working through the performance method parameters for an early 1900s historic downtown building. We typically use the work area method, but unfortunately that won't work for this building. The building has 3 stories + a basement, 48' height, with S-1 in the basement, M on the ground floor, B on the second floor, and R-3 (two units) on the top floor. S-1 and M are nonseparated. B and R-3 are separated by 1 hour floors and walls. The ground floor is 3000 SF, all other levels are 1500 SF each. The ground floor (M) is the only occupancy in our scope - it was previously an art gallery, so change of occupancy plus some MEP work. Exterior walls are 24" masonry. Building type is III-B and all floors are sprinklered. I am using the NC 2018 EBC, which is based on the 2015 IEBC.
The building is well within the allowable area for each level, so I'm not concerned, but I do need to work out the exact number of points for this parameter. The snag I'm hitting is that I need to divide actual area by allowable area for each occupancy (per NC EBC 1401.6.2 and its subsections), but R-3's allowable area is unlimited. How do I work "unlimited" into the formula? Am I missing something simple here?
The building is well within the allowable area for each level, so I'm not concerned, but I do need to work out the exact number of points for this parameter. The snag I'm hitting is that I need to divide actual area by allowable area for each occupancy (per NC EBC 1401.6.2 and its subsections), but R-3's allowable area is unlimited. How do I work "unlimited" into the formula? Am I missing something simple here?