Checking in here for some feed back. I have found this code relating to pex as a TPR tube. However a property manager has asked around with several plumbers and all of them seem to believe that using 3/4 Pex with crimp connections is okay. I want to make sure I'm interpreting this correctly. Is this is requiring a one inch TPR tube?
P2804.6.1- Point 3 and 14 are relevant.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
14. Be one nominal size larger than the size of the relief-valve outlet, where the relief valve discharge piping is installed with insert fittings. The outlet end of such tubing shall be fastened in place.
If using PEX, the pipe must be one nominal size larger than the size of the relief-valve outlet, where the relief valve discharge piping is installed with insert fittings. The outlet end of such tubing shall be fastened in place.
P2804.6.1- Point 3 and 14 are relevant.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
14. Be one nominal size larger than the size of the relief-valve outlet, where the relief valve discharge piping is installed with insert fittings. The outlet end of such tubing shall be fastened in place.
If using PEX, the pipe must be one nominal size larger than the size of the relief-valve outlet, where the relief valve discharge piping is installed with insert fittings. The outlet end of such tubing shall be fastened in place.