PIPING IN COMMON TRENCH
Rider Rick
True or false?
2006 IRC P2904.4.1 Water and sewer OK in same trench if both materials approved for use in the building.
Thank you,
Rick
Re: PIPING IN COMMON TRENCH
True!
You can have them in the same trench even if they aren't approved for use under the building. The water line would have to be put on a shelf.
EDIT!!!!! This may be a trick question........."in" a building???
They can both be in the same trench if approved for use "under" a building.
P2904.4.2 Water service installation. Trenching, pipe
installation and backfilling shall be in accordance with Section
P2604.Water-service pipe is permitted to be located in
the same trench with a building sewer provided such sewer
is constructed of materials listed for underground use within
a building in Section P3002.1. If the building sewer is not
constructed of materials listed in Section P3002.1, the
water-service pipe shall be separated from the building
sewer by a minimum of 5 feet (1524 mm), measured horizontally,
of undisturbed or compacted earth or placed on a
solid ledge at least 12 inches (305 mm) above and to one
side of the highest point in the sewer line.
Rick,
"2006 IRC P2904.4.1 Water and sewer OK in same trench if both materials approved for use in the building."
My 2006 IRC puts it in P2904.4.2 Water Service Installation.
"Water-service pipe is permitted to be located in the same trench with a building sewer provided such sewer (refers to sewer pipe only; not water) is constructed of materials listed for underground use within a building in Section P3002.1 (Table P3002..1(2))"
When adopting the IRC; the above should be deleted; and the more restrictive requirement that follows in P2904.4.2, should be enforced;
" The water-service pipe shall be separated from the building sewer by a minimum of 5 feet, measured horizontally, of undisturbed (delete "or compacted") earth or placed on a SOLID ledge at least 12 inches above and to one side of the hightest point in the sewer line."
Building sewer line leaks are inevitable; and because water-service lines (especially PVC) will also experience leaks; allowing them in the same trench will guarantee an eventual contamination of the water supply system.
However, to answer your question; if the sewer service material, meets the requirements of P3002.1; yes, the incompetent installer, that is installing it can put the water-service line, in the same trench with the sewer.
Uncle Bob
Thank you Uncle Bob,
The incompetent installer meets code when ABS sewer line with the copper water main is together at the bottom of a 12" wide trench?
Thank you,
Rick
Rick Taylor said:
Thank you Uncle Bob,The incompetent installer meets code when ABS sewer line with the copper water main is together at the bottom of a 12" wide trench?
Thank you,
Rick
Hmmmmmph! That's okay......My feelings aren't hurt! :(
Rick,
"The incompetent installer meets code when ABS sewer line with the copper water main is together at the bottom of a 12" wide trench?" Yes, ABS DWV Schedule 40 IPS pipe, solid and/or cellular core, per Table P3002.1(2).
Sorry, ya'll,
Having a bad hair day. I was thinking of licensed plumbers who know better; and do it anyway because it saves them money and increases their profit.
My bad. :(
Uncle Bob
As a Building inspector do we have to approve it because it meets the code?
Rick
Rick,
Unfortunately, yes; we cannot fail the inspection.
Uncle Bob
Rick, see post # 3...........
And yes....as inspectors we would have to pass it as compliant with the codes.
Pwood! You win the Monday first place award! That allows you to answer first on the next question regarding plumbing requirements for same trench location if asked on Tuesday. :lol:
Mule! Congrats you got second! Sorry no prize. :)
UB: You get a blue ribbon for the longest yes answer! :D
From RJJ! The answer is yes!
RJJ,
And I get to approve potable water line and sewer line in same ditch.
Rick