lpiburn
Silver Member
Hello all,
I'm trying to figure out when PIVs are required to be monitored.
The local authority is essentially a volunteer fire department, so I don't have anyone official to ask. From what I understand, a Post Indicator Valve is only required if stipulated by the local AHJ and/or fire department. In this case there is no such requirement, but the contractor installed a PIV anyway. Unfortunately, they forgot to add the monitoring system. Now they are refusing to add it without additional compensation, even though they had submitted monitoring with the system.
Scope of work arguements and legal stuff aside, I'm having dificulty finding where (if at all) it is required for PIVs to be monitored by the alarm system. The closest I could come up with is this:
IFC 903.4:
The project is for a small dental clinic. Type B occ. Less than 5000 s.f. so technically neither sprinklers or alarms are required at all. That said, the system is in place (flow is monitored) and we want to make darn sure everything is compliant. Does it make any difference if the PIV is not required by code to begin with? Is it one of those situations where "when provided, ______ shall comply with..."?
Thanks in advance.
-LP
I'm trying to figure out when PIVs are required to be monitored.
The local authority is essentially a volunteer fire department, so I don't have anyone official to ask. From what I understand, a Post Indicator Valve is only required if stipulated by the local AHJ and/or fire department. In this case there is no such requirement, but the contractor installed a PIV anyway. Unfortunately, they forgot to add the monitoring system. Now they are refusing to add it without additional compensation, even though they had submitted monitoring with the system.
Scope of work arguements and legal stuff aside, I'm having dificulty finding where (if at all) it is required for PIVs to be monitored by the alarm system. The closest I could come up with is this:
IFC 903.4:
This is somewhat confusing because it is within section 903 on the sprinkler system itself, not 507 fire protection water supplies. If I am reading this right, all valves controlling water flow to the system all the way out to the main would have to be monitored, even if they are a regular shut-off valve and not a PIV. Can that be correct?All valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures and water-flow switches on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit.
The project is for a small dental clinic. Type B occ. Less than 5000 s.f. so technically neither sprinklers or alarms are required at all. That said, the system is in place (flow is monitored) and we want to make darn sure everything is compliant. Does it make any difference if the PIV is not required by code to begin with? Is it one of those situations where "when provided, ______ shall comply with..."?

Thanks in advance.
-LP