Places of assembly, NEC or IBC.

jumper

Bronze Member
Joined
Dec 9, 2009
Messages
35
Location
Easton MD NEC 2008
When considering wiring methods, which would apply for determining which code decides on the occupancy. IBC 303.1 says 50 people, but NEC 518.1 says 100 people.

State has adopted IBC and 2701.1 just says follow NFPA 70.
 
Here's the section in the VA USBC;

101.6 Order of precedence. The provisions of Chapter 1 of this code supersede any conflicting provisions of Chapters 2– 35 of the IBC and any conflicting provisions of the codes and standards referenced in the IBC. In addition, the state amendments to the IBC supersede any conflicting provisions of Chapters 2–35 of the IBC and any conflicting provisions of the codes and standards referenced in the IBC. Further, the provisions of Chapters 2–35 of the IBC supersede any conflicting provisions of the codes and standards referenced in the IBC.
 
You are mixing apples with oranges.

The building code designates occupancy type, not the NEC. The IBC may classify a building or space as an assembly, but that building or space only needs to comply with Article 518 of the NEC if it meets the 100 person provision. Group A's of less than 100 persons need not meet Article 518 but are still assemblies.

This type of thing can happen with health care facilities as well. The IBC may classify an occupancy as a Group B, but may be a health care facility as far as the NEC is concerned.
 
Thanks Bryan

Exceptions are always a rule for general statements "in cases where the code establishes a specific requirement for a certain condition, that requirement is applicable even if it is less restrcitve than a general requirement elsewhere in the code." The most restrictive applies to the manufacturer's listing or installations.
 