I am working on an adaptive re-use project converting a retail building into a dance school. Two of the studios will be larger and sometimes have rehearsals with larger groups, they have occupant loads of over 50 and will be considered A3. The remaining studios are smaller and have occupant loads under 50 so are considered B occupancy. My question is when I do the plumbing fixture calculations can I use the assembly type ratio for all the studios, even the ones that fall under type B occupancy? 2902.1 says the plumbing fixtures shall be provided "based on the actual use of the building space" The fixture count when all the small assembly spaces are calculated as business areas seems disproportionately high and the use of the space is not at all like business/office space.
The lobby and reception areas are also assembly type spaces, but with occupant loads of under 50. Would/could these areas also be an assembly spaces for the plumbing fixture counts or business? We are already adding two restrooms for a total of 4.
This project is 2018 IBC/IPC