Hi all,
I am with a design firm working on a renovation project for an existing hospital. We are going to be doing a major renovation to the emergency department and I am having trouble applying plumbing fixture requirements. Using vanilla IBC 2018 Chapter 29.
The institutional category is broken down into subcategories (detention not applicable here)
1. Custodial care facilities
2. Medical care recipients in hospitals and nursing homes
3. Employees in hospitals and nursing homes
4. Visitors in hospitals and nursing homes
#2 sounds right, but the W/C requirement is simply one-per-room. That doesn't make sense in an emergency room setting. It is clearly for hospital inpatients. Should I use custodial care which is 1/10 occupants?
#3 for employees is also confusing to me. All the occupancy calculations in the code are simply based on square footage. I can go to the hospital Owner and see what their planned staffing is for the area, but there is no place I can find in the plumbing portion of the code which says that is OK. Assuming it is, would the staff count be subtracted from the calculated occupant load for the department in order to figure out the visitor count?
I also looked in the 2012 UPC which I happened to have a copy of. It breaks things down differently:
1. hospitals and nursing homes - individual rooms and ward room
1a. 1 per room
1b. 1 per 8 patients
2. hospital waiting or visitor rooms - 1 per room
3. Employee use - (complicated, based on occ load)
So I guess in the UPC an emergency room would be considered a "ward room"?
Any advice on the topic would be appreciated.
I am with a design firm working on a renovation project for an existing hospital. We are going to be doing a major renovation to the emergency department and I am having trouble applying plumbing fixture requirements. Using vanilla IBC 2018 Chapter 29.
The institutional category is broken down into subcategories (detention not applicable here)
1. Custodial care facilities
2. Medical care recipients in hospitals and nursing homes
3. Employees in hospitals and nursing homes
4. Visitors in hospitals and nursing homes
#2 sounds right, but the W/C requirement is simply one-per-room. That doesn't make sense in an emergency room setting. It is clearly for hospital inpatients. Should I use custodial care which is 1/10 occupants?
#3 for employees is also confusing to me. All the occupancy calculations in the code are simply based on square footage. I can go to the hospital Owner and see what their planned staffing is for the area, but there is no place I can find in the plumbing portion of the code which says that is OK. Assuming it is, would the staff count be subtracted from the calculated occupant load for the department in order to figure out the visitor count?
I also looked in the 2012 UPC which I happened to have a copy of. It breaks things down differently:
1. hospitals and nursing homes - individual rooms and ward room
1a. 1 per room
1b. 1 per 8 patients
2. hospital waiting or visitor rooms - 1 per room
3. Employee use - (complicated, based on occ load)
So I guess in the UPC an emergency room would be considered a "ward room"?
Any advice on the topic would be appreciated.