electrical plan review is the way to go. If the construction documents are produced on a drawing (cad) program then there is no reason to not submit them electronically for review and storage. We use BlueBeam
https://www.bluebeam.com/solutions/revu to mark up plans. check it out
Also check with your states minimum requirements
Start with code required minimum inspections
IBC
[A] 110.3 Required inspections.
The building official, upon notification, shall make the inspections set forth in Sections 110.3.1 through 110.3.10.
[A] 110.3.1 Footing and foundation inspection.
Footing and foundation inspections shall be made after excavations for footings are complete and any required reinforcing steel is in place. For concrete foundations, any required forms shall be in place prior to inspection. Materials for the foundation shall be on the job, except where concrete is ready mixed in accordance with ASTM C 94, the concrete need not be on the job.
[A] 110.3.2 Concrete slab and under-floor inspection.
Concrete slab and under-floor inspections shall be made after in-slab or under-floor reinforcing steel and building service equipment, conduit, piping accessories and other ancillary equipment items are in place, but before any concrete is placed or floor sheathing installed, including the subfloor.
[A] 110.3.3 Lowest floor elevation.
In flood hazard areas, upon placement of the lowest floor, including the basement, and prior to further vertical construction, the elevation certification required in Section 1612.5 shall be submitted to the building official.
[A] 110.3.4 Frame inspection.
Framing inspections shall be made after the roof deck or sheathing, all framing, fireblocking and bracing are in place and pipes, chimneys and vents to be concealed are complete and the rough electrical, plumbing, heating wires, pipes and ducts are approved.
[A] 110.3.5 Lath and gypsum board inspection.
Lath and gypsum board inspections shall be made after lathing and gypsum board, interior and exterior, is in place, but before any plastering is applied or gypsum board joints and fasteners are taped and finished.
Exception: Gypsum board that is not part of a fire-resistance-rated assembly or a shear assembly.
[A] 110.3.6 Fire- and smoke-resistant penetrations.
Protection of joints and penetrations in fire-resistance-rated assemblies, smoke barriers and smoke partitions shall not be concealed from view until inspected and approved.
[A] 110.3.7 Energy efficiency inspections.
Inspections shall be made to determine compliance with Chapter 13 and shall include, but not be limited to, inspections for: envelope insulation R- and U-values, fenestration U-value, duct system R-value, and HVAC and water-heating equipment efficiency.
[A] 110.3.8 Other inspections.
In addition to the inspections specified in Sections 110.3.1 through 110.3.7, the building official is authorized to make or require other inspections of any construction work to ascertain compliance with the provisions of this code and other laws that are enforced by the department of building safety.
[A] 110.3.9 Special inspections.
For special inspections, see Chapter 17.
[A] 110.3.10 Final inspection.
The final inspection shall be made after all work required by the building permit is completed.
[A] 110.3.10.1 Flood hazard documentation.
If located in a flood hazard area, documentation of the elevation of the lowest floor as required in Section 1612.5 shall be submitted to the building official prior to the final inspection.
IRC
R109.1 Types of inspections.
For onsite construction, from time to time the building official, upon notification from the permit holder or his agent, shall make or cause to be made any necessary inspections and shall either approve that portion of the construction as completed or shall notify the permit holder or his or her agent wherein the same fails to comply with this code.
R109.1.1 Foundation inspection.
Inspection of the foundation shall be made after poles or piers are set or trenches or basement areas are excavated and any required forms erected and any required reinforcing steel is in place and supported prior to the placing of concrete. The foundation inspection shall include excavations for thickened slabs intended for the support of bearing walls, partitions, structural supports, or equipment and special requirements for wood foundations.
R109.1.2 Plumbing, mechanical, gas and electrical systems inspection.
Rough inspection of plumbing, mechanical, gas and electrical systems shall be made prior to covering or concealment, before fixtures or appliances are set or installed, and prior to framing inspection.
Exception: Backfilling of ground-source heat pump loop systems tested in accordance with Section M2105.1 prior to inspection shall be permitted.
R109.1.3 Floodplain inspections.
For construction in flood hazard areas as established by Table R301.2(1), upon placement of the lowest floor, including basement, and prior to further vertical construction, the building official shall require submission of documentation, prepared and sealed by a registered design professional, of the elevation of the lowest floor, including basement, required in Section R322.
R109.1.4 Frame and masonry inspection.
Inspection of framing and masonry construction shall be made after the roof, masonry, all framing, firestopping, draftstopping and bracing are in place and after the plumbing, mechanical and electrical rough inspections are approved.
R109.1.5 Other inspections.
In addition to the called inspections above, the building official may make or require any other inspections to ascertain compliance with this code and other laws enforced by the building official.
R109.1.5.1 Fire-resistance-rated construction inspection.
Where fire-resistance-rated construction is required between dwelling units or due to location on property, the building official shall require an inspection of such construction after all lathing and/or wallboard is in place, but before any plaster is applied, or before wallboard joints and fasteners are taped and finished.
R109.1.6 Final inspection.
Final inspection shall be made after the permitted work is complete and prior to occupancy.
R109.1.6.1 Elevation documentation.
If located in a flood hazard area, the documentation of elevations required in Section R322.1.10 shall be submitted to the building official prior to the final inspection.