Let me clarify. This gate does swing out away from the pool. It is in a common area. There are 3 buildings that share 2 pools. Everything is outside.When you say “IN condo”, do you mean it’s a private pool serving a single condo unit, or is it the common area pool serving many condos?
If the latter and it was in California, you would be required to have free exit away from the pool - - no key or special knowledge required.
Is an outside gate for a fence considered a door or egress door?See fatboy's post, above. The need to use a key fob to exit is not allowed.
Is an outside gate for a fence considered a door or egress door?
If this part of the means of egress, I would certainly allow a designer to treat it like a door. Alternatively, I don't care what it is called. It is simply an obstruction to the means of egress.Is an outside gate for a fence considered a door or egress door?
And it does not seem to meet the latch height requirement...
305.3.3 Latch release. For doors and gates in barriers,
the door and gate latch release mechanisms shall be in
accordance with the following:
2. Where door and gate latch release mechanisms are
of the self-locking type such as where the lock is
operated by means of a key, an electronic opener
or the entry of a combination into an integral
combination lock, the lock operation control and
the latch release mechanism shall be located
above the finished floor or ground surface in
accordance with the following:
2.1. At public pools and spas, not less than 34
inches and not greater than 48 inches
(1219 mm).
2.2. At residential pools and spas, at not greater
than 54 inches (1372 mm).
But I have another wrinkle to throw into the mix: do your ADA regulations apply in this case? Is a magnetic foblet compliant with latch/handle regulations?
What latch?
View attachment 14180
The release that Yankee already pointed out....If it is public...Might be OKWhat latch?
View attachment 14180
It is a magnetic lock. There is no latch assembly. So there......................The doohickey that's released by the key fob gizmo.
Exits from the building are out the front and rear and one or two come out to the pool area.Are there adequate exits through the building or are these gates the only exits?
1010.2.11 Door Hardware Release of Electrically Locked Egress DoorsIt is a magnetic lock. There is no latch assembly. So there......................
When you are in the pool area and you go out of a required exit gate, does that path (A) lead you into the adjacent building before you exit discharge?Exits from the building are out the front and rear and one or two come out to the pool area.
I did not do the math, but eyeballing it I'm guessing OL>50, so panic hardware required based on deck space.
DING DING DING......ARE THEY REQUIRED EXITS? Not yelling but not fixing the caps either.....Exits from the building are out the front and rear and one or two come out to the pool area.
That is an awesome question. I don't know.DING DING DING......ARE THEY REQUIRED EXITS? Not yelling but not fixing the caps either.....
If so they need to provide access to the public way or the exterior area discharge ( 50 ft away 5sqft per person) and meet all of the Egress requirements for the building w/o discussing any pool OL.......That is an awesome question. I don't know.