• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Prep for fuel island

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,069
Location
Somewhere Too Hot & Humid
Initially the engineer spec'd out the RMC to be 18" below the finished grade to and at the pumps. I suppose he forgot the 24" requirement.

Anyway, these guys were bending conduit and placing the raceway seals in single digit temperatures. Here is a look at what they have done so far.

514-2.jpg
 
Re: Prep for fuel island

Jeff did they run RMC @ 24" Below grade all the way to fuel dispensing pump or did they convert to PVC per 514.8 exception.....Just asking.
 
Re: Prep for fuel island

Are those conduit-stretchers... er, I mean couplings listed for wet locations?
 
Re: Prep for fuel island

jar546 said:
Initially the engineer spec'd out the RMC to be 18" below the finished grade to and at the pumps. I suppose he forgot the 24" requirement.
The EC didn't catch that?
 
Re: Prep for fuel island

chris kennedy said:
jar546 said:
Initially the engineer spec'd out the RMC to be 18" below the finished grade to and at the pumps. I suppose he forgot the 24" requirement.
The EC didn't catch that?

No, I caught that at plan review. I am sure the EC would have caught it too but since I saw it on the plans..............
 